Question 1,077 of 1,128

For a pneumatic transmission system for instrumentation purposes, if a pneumatic instantaneous flow indicator has a calibrated scale of 0 to 1000 gpm, what would be the actual measured instantaneous flow rate if the transmitted pneumatic signal pressure to the indicator is 9 psig, assuming the industry standard of 3 to 15 psig is used for instrument air?

0 ✓ | 0 ✕ 10 free left today

Tip: press A-D to answer

More General Subjects questions

Mariner discussion

Comments from mariners who studied this question.

ma magnussonshred · Sep 14, 2016
What's the equation for this one?
by bybymsn · Sep 16, 2016
The regulator range is 3-15 psi, a difference of 12 psi. So, since 3 psi is the minimum an input of 9 psi would actually be 50% (9 psi minus 3= 6 psi). And 50% of 1000 is 500 rpm. What they're talking about is a pneumatically controlled flow valve. One of these: