| As shown in the illustrated electronic overload relay, if the full load amp setting accurately represents the motor full load current of 6 amps and the trip class dip switch settings are for a trip class of 20, what statement is true assuming that the locked rotor current is 6 times the full load current. |
| A) The relay will trip in 20 seconds or less at a current equal to 36 amps. |
| B) The relay will trip in 36 seconds or less at a current equal to 120 amps. |
| C) The relay will trip in 20 seconds or less at a current equal to 6 amps. |
| D) They relay will trip in 36 seconds or less at a current equal to 20 amps. |