| As shown in the illustrated electronic overload relay, if the full load amp setting accurately represents the motor full load current of 10 amps and the trip class dip switch settings are for a trip class of 10, what statement is true assuming that the locked rotor current is 6 times the full load current. |
| A) The relay will trip in 10 seconds or less at a current equal to 100 amps. |
| B) The relay will trip in 60 seconds or less at a current equal to 10 amps. |
| C) The relay will trip in 10 seconds or less at a current equal to 60 amps. |
| D) They relay will trip in 60 seconds or less at a current equal to 100 amps. |