Engine : Refrigeration AC - 933/610
Get a hint
« Previous Question
You are checking the supply chilled water temperature thermistor probe on a high-pressure hermetic centrifugal chiller. Using the illustrated chart, what statement is true if the supply water temperature is verified 45°F with a digital thermometer? Illustration GS-RA-48
A) When checked with control power off and the thermistor probe isolated, the thermistor probe voltage drop should be 3.805 volts.
B) When checked with control power on and the thermistor probe isolated, the thermistor probe voltage drop should be 3.805 volts.
C) When checked with control power on and the thermistor probe connected into the circuit, the thermistor probe voltage drop should be 11.416 volts.
D) When checked with control power on and the thermistor probe connected into the circuit, the thermistor probe voltage drop should be 3.805 volts.
loading answer...
The U.S. Coast Guard has not yet released this Illustration.