The winch shown in the illustration will operate normally in all speeds in both directions, with the exception that it will not accelerate into 'fifth point' hoist or 'fifth point' lower. What would be a possible cause? Illustration EL-0102 |
A) master switch contacts "MS 8' are welded closed |
B) time delay relay '3T' coil is open-circuited |
C) master switch contact 'MS 7" fails to close |
D) the contactor '5A' coil is open-circuited |
loading answer...